3 Basic Modes of Power Factor Testing Explained

3 Basic Modes of Power Factor Testing Explained
Testing power factor is a means of measuring the integrity of the insulation. Photo: Doble Engineering.

Most failures of electrical power equipment are the result of a breakdown in the insulation system. To keep failures at a minimum, periodic maintenance testing of the insulation is recommended to indicate whether it is deteriorating, and how fast.

Power factor tests are used to measure dielectric losses, which relate to the wetness, dryness or deterioration of electrical insulation.

Power factor is defined as the cosine of the phase angle between voltage and current. For an ideal insulation, the phase angle is 90°. In practice no insulation is ideal, but instead has a certain amount of loss, and the total current leads the voltage by a phase angle less than 90°


How is Power Factor Measured?

Measuring insulation power factor is achieved by calculating the ratio of the capacitive or "charging" current (measured in voltamperes) to resistive or "leakage" current (measured in watts).

Vector Components of Test Voltage and Currents in a Parallel R/C Circuit
Vector Components of Power Factor Test Voltage and Current. Photo: Doble Engineering.

Testing power factor is a means of measuring the integrity of the insulation, since the smaller the power factor, the better the insulator. This is one of the best testing techniques for predictive and preventive maintenance.

Power factor testing also makes it possible to detect equipment insulation problems without making an internal visual inspection. The result is a significant decrease in maintenance cost and downtime.

The power factor test set utilizes an AC voltage and comes with three basic modes of operation:

  1. GST - Grounded Specimen Test
  2. GST Guard Mode - Guarded Specimen Test
  3. UST - Ungrounded Specimen Test

Power Factor Test Set Leads

When considering the three different modes of operation, it is important to understand which test leads are associated with each mode. Power factor test sets have four different leads for connecting to the device under test:

Power factor test sets have four test leads
Power factor test sets have four different leads for connecting to the device under test. Photo: TestGuy

  • High Voltage Output Lead - Supplies the voltage necessary to produce the test current. Not specific to any mode of operation. Power Factor testing is typically performed at 10 kV or values equivalent to 10 kV are obtained.
  • Ground Return Lead (GST) - Measures current flowing through the ground path.
  • Red/Blue Leads (UST) - Used to guard out current not flowing through the ground path. Examples of this would be the leakage between the high side winding and low side winding of a transformer or the current leaking between the line side and the load side of an open circuit breaker. Of the two UST leads, only one is actually used in over 95% of the practical application.

Three Modes of Power Factor Testing

When you break it all down, it's really quite simple. There are two paths of leakage current returning to the test set, ground or guard.

Power factor test mode examples
When considering the three different modes of the power factor test set, it is important to understand which test leads are associated with each mode. Photo: Doble.

The GST Guard tests measures the total current leaking to ground only. The power factor test set ignores current flowing through the red or blue lead.

Inversely, in UST mode, ground is considered guard since grounded terminals are not measured. When the UST test is performed, the only current being measured by the test set is the current flowing on the red or blue lead. Any current flowing to a grounded terminal is bypassed directly to the AC source return and is eliminated from the measurement.

UST mode is used to measure insulation between two ungrounded terminals of the apparatus, isolate an individual section of insulation and test it without measuring other connected insulation.

In the last mode of operation, the GST mode, both leakage paths (ground lead and the red or blue lead) are measured by the test set. The current, watts loss, and capacitance parameters of the UST and GST Guard tests should equal the parameters in the GST test. This gives the overall condition or power factor of the test specimen.

If the sum of the UST and GST guarded parameters do not equal the GST parameters, then either the test set is malfunctioning or the test leads are configured incorrectly.


References