Report Tech Quiz Issues Here

3. You are asked to analyze a thermographic image of a single insulated electrical connection under 60% load, the ambient temperature recorded was 72°F and temperature points on the image indicate a temperature of 112°F at the connection in question, what would be the appropriate action level?
Your Answer: Warrants investigation
Correct Answer: Monitor until corrected
Help: NETA Table 100.18

question in F, table in C.