- To increase the power factor of a substation 750 kVA load that has a 0.76 PF to a PF of 0.95, which of the following capacitor banks would provide desired power factor?**
Your Answer: 250 kVAR
Correct Answer: 300 kVAR
PLease explain
PLease explain
I think your answer of 250kVAR is correct.
Key formula for this question is
Q = S x sin(cos-1(pf))
750kVA at 0.76PF
Q = 750 x sin(cos-1(0.76))
Q = 750 x sin(40.54)
Q = 750 x 0.65
Q = 487.44
750kVA at 0.95PF
Q = 750 x sin(cos-1(0.95))
Q = 750 x sin(18.19)
Q = 750 x 0.312
Q = 234.18
Correction = 487.44 - 234.18
Correction = 253.26
Your solution assumes that the apparent power (S) is held constant. For power factor correction, true power (P) is held constant.
Let:
PF1 = original power factor
PF2 = desired power factor
P = True Power
Q1 = Original Reactive Power
Q2 = Desired Reactive Power
Qc = Capacitor Bank Reactive Power
S1 = Original Apparent Power
S2 = Desired Apparent Power
For this problem,
P = S1 * PF1 = 750kVA * 0.76 = 570 kW
S2 = P / PF2 = 570kW / 570 = 600kVA
Q1 = SQRT(S1^2 - P^2) = 487 kVAR
Q2 = SQRT(S2^2 - P^2) = 187 kVAR
Qc = Q1 - Q2 = 487 - 187 = 300 kVAR
I noticed a slight mistake on the line calculating S2. It should be 570kW / 0.95 = 600kVA
This website is not affiliated with, maintained, authorized, endorsed or sponsored by the International Electrical Testing Association (NETA) or any of its affiliates. The information presented on this website should not be used to replace any kind of classroom or group study led by a certified instructor. The use of all copyrighted material on this website is provided for the purposes of teaching, scholarship, and research, and is therefore considered to be covered as "fair use" as specified in 17 USC § 107 - Limitations on exclusive rights: Fair use. If you are the owner of copyrighted material on this website and feel that our use of such material is not covered under 17 USC § 107, please contact us. TestGuy.net is a participant in the Amazon Services LLC Associates Program, an affiliate advertising program designed to provide a means for sites to earn advertising fees by advertising and linking to amazon.com. Copyright © 2026 TestGuy.net. All rights reserved.